Cannot find anywhere to set the Modbus Station ID.
I have a couple modbus RTU devices on the over side of a Modbus RTU to Modbus TCP gateway and I need to set the ID's to see them,
I have it working in VTscada Lite. Which you can use free for 50 tags. CHangeset attached in a zip file because this forum doesn't recognise .changeset files.
Modbus TCP through a gateway
-
- Posts: 5
- Joined: Sun May 13, 2018 2:32 pm
Modbus TCP through a gateway
- Attachments
-
- TempetureBox.zip
- (123.76 KiB) Downloaded 193 times
Re: Modbus TCP through a gateway
Hello
I will probably add the possibility of selecting the ID Unit on the Mobdus connection control in a future update, but this will not happen before 2 or 3 months.
Regards.
I will probably add the possibility of selecting the ID Unit on the Mobdus connection control in a future update, but this will not happen before 2 or 3 months.
Regards.
Re: Modbus TCP through a gateway
New Suppanel version 1.19 available from January 4, 2021.
It allows optionally to select a slave ID in the Modbus address.
For example: without ID the address 400001 has by default slave ID equal to 1, but if we put 23/400001 then slave ID will be equal to 23 for this variable
It allows optionally to select a slave ID in the Modbus address.
For example: without ID the address 400001 has by default slave ID equal to 1, but if we put 23/400001 then slave ID will be equal to 23 for this variable